I'm about to present some data from my energy model and need to know if there are additional processes I need to perform similar to the COP calculations.
I have been wondering if my total heat load is accounting for internal gains through lighting, people, and equipment. Is this accounted for or do I need to subtract these units?
I also assume that my total heating and cooling is accounting for solar gain. I have tested this and believe it is.
Anything else I'm missing to get good numbers out?
Tags:
Replies are closed for this discussion.
David,
I am not sure if I am understanding your question but energyplus is running an energy balance calculation that accounts for all of the terms that you see in this chart:
http://hydrashare.github.io/hydra/viewer?owner=chriswmackey&for...
If you are looking for output heating and cooling in units of electricity/fuel rather than heating/cooling load, I suggest that you run your modyl with a real HVAC system instead of the default ideal air loads as you see in this example file:
http://hydrashare.github.io/hydra/viewer?owner=chriswmackey&for...
This will likely be much more accurate than multiplying your ideal air loads by a COP.
-Chris